Architectural Coatings | American Coatings Association Coatings Protect. Coatings Preserve. Coatings Provide. Fri, 27 Feb 2026 20:38:55 +0000 en-US hourly 1 https://wordpress.org/?v=6.7.4 /wp-content/uploads/2019/09/cropped-fav-150x150.png Architectural Coatings | American Coatings Association 32 32 Formulation Flexibility and Enhanced Performance in Architectural Coatings without Relying on Fluorinated Additives /coatingstech-magazine/articles/formulation-flexibility-and-enhanced-performance-in-architectural-coating-without-relying-on-fluorinated-additives/ Thu, 26 Feb 2026 20:48:56 +0000 /?post_type=ct_articles&p=255332 Robert W. Sandoval, EPS – Engineered Polymer Solutions

Introduction

Per- and polyfluoroalkyl substances (PFAS) have been used historically in paint formulations for their hydrophobic and oleophobic properties in addition to their surface properties. In waterborne coating formulations, they are often present as fluorosurfactants (FS). This study explores the development of high-performance waterborne coatings that do not require fluorosurfactants and maintain or exceed the performance of legacy FS-containing systems.

Architectural coatings are expected to deliver a balance of performance properties. Among the most critical performance attributes is block resistance, especially in high-traffic and high-touch environments such as kitchens, bathrooms, cabinetry, and institutional settings. Removing fluorosurfactant from formulations often leads to trade-offs in performance, particularly in block resistance, tack resistance, and durability. Traditional approaches to improve block resistance, such as increasing pigment volume concentration (PVC), raising glass transition temperature (Tg), or adding waxes, can negatively impact gloss, durability, or VOC content. Therefore, another approach is necessary.

By optimizing polymer design, focusing onTg, particle morphology, crosslinking, and monomer selection, this research demonstrates that coatings can achieve excellent block resistance, tack resistance, washability, and durability without the use of fluorosurfactants. Comparative performance data across gloss levels and environmental conditions validate the efficacy of these optimized systems, offering a resin-based approach to eliminating FS from waterborne acrylic coating formulations.

This article presents a comprehensive study on the development of an optimized all-acrylic polymer system that eliminates fluorinated additives while maintaining or improving key performance metrics.

Materials and Methods

This study focuses on an all-acrylic polymer that does not contain fluorosurfactant while delivering high-performance properties. A high-gloss (HG) polymer was specifically designed to achieve gloss levels above 80 GU at 60°, with a minimum film formation temperature (MFFT) of 21 °C and utilizing self-crosslinking monomer.

Resins with higherTgor elevated MFFT typically exhibit desirable hardness characteristics, such as reduced surface tack. However, increasing hardness often requires additional coalescent, which can raise VOC levels in the final coating formulation. To balance these factors, the HG polymer was engineered to minimize coalescent demand while maintaining surface performance. The incorporation of a self-crosslinking monomer further enhanced hardness without increasing VOC content, as crosslinking occurred after film formation rather than during application. The resin system was evaluated against an FS-containing control resin.

Four coating base formulations using the optimized polymer are shown inTable 1. The deep base formulas in this study were tinted with 12 oz of colorant per 100 gal.

Experimental

The following tests were conducted.

Hot Block Resistance

Hot block resistance was evaluated with a 3-mil drawdown dried at 70 °F and 50% relative humidity (RH). Small squares were cut at dimensions of 1.5 in. by 1.5 in. and the coated sides were placed together and put in a 120 °F oven with a 1000 g weight on top. Then, samples were kept at room temperature for 30 min before the samples were pulled apart and the block resistance was rated on a scale of 0-10, with a rating of a 0 indicating fully adhered, and a rating of 10 indicating no adhesion and the squares pulled apart from each other with essentially no force needed.

Cotton Ball Tack Resistance

The tack resistance of the HG surface was evaluated by allowing the coated sample to dry for 24 h under controlled conditions of 70 °F and 50% RH. After drying, a cotton ball was placed on the surface, and a 500 g weight was applied directly on top. The setup was then transferred to an oven and exposed to 120 °F for 60 min. Following heat exposure, the sample was allowed to rest at room temperature for 30 min. After this rest period, the cotton ball was removed and evaluated for cotton residue.

High-Traffic Durability

The “light switch test” was conducted to simulate high traffic and high contact conditions. Lotion was applied to half of each test panel and allowed to sit for 2 h. After the exposure period, the lotion was wiped off, and the panels were stained with a combination of mineral oil and a dirt particulate, as well as a rusty water solution. These stains were allowed to dry for 2 h before being wiped with a paper towel. The panels were then subjected to 100 wash cycles using a sponge and a nonabrasive scrub medium. Finally, the color change (ΔE) of the stains was measured to assess the coating’s chemical resistance and ability to resist softening and staining.Figure 1shows a panel that was prepared and washed.

]]>
Colorant Effects on Solar Reflectivity and Rheology of Exterior Architectural Coatings /coatingstech-magazine/articles/colorant-effects-on-solar-reflectivity-and-rheology-of-exterior-architectural-coatings/ Wed, 27 Aug 2025 19:24:45 +0000 /?post_type=ct_articles&p=252500 By Ray Fernando, Olivia Everitt, and Caleb Hall California Polytechnic State University

The main objective of this study is to generate formulating knowledge that can be applied for selecting appropriate solar reflective pigments and fillers for exterior wall coatings of various colors while retaining other important coating properties. A low pigment volume concentration (PVC), all acrylic, white formulation was used as the tint base for all colorants, conventional and infrared (IR) reflective. The key tests included rheology of the wet paints and color, gloss, hiding, and solar reflectance of dry coating films. Commercially available solar reflective materials, such as hollow spherical inorganic and organic particulate fillers and mixed-metal-oxide black and other color pigments and their equivalent conventional pigments were studied. Particular attention was focused on the issue of viscosity instability of tint base when tinted with colorants. Solar reflectance gains from IR-reflective pigments will be presented in comparison to coatings of the same color and other properties, formulated with conventional colorants. Results of this study can be used to estimate cooling energy savings due to incorporation of IR-reflective pigments.

Introduction

The earth receives about 50% of its solar power in the form of ultraviolet (UV) and visible radiation whereas the remaining 50% is in the form of infrared (IR).1 The need for solar power to sustain all forms of life on earth is an unarguable fact. However, excessive amounts of solar power can cause harmful effects. An example of this is the phenomenon known as the heat-island effect.2 Within a highly developed urban center, roofs and pavements receive and trap excessive amounts of solar energy in the form of heat causing greater needs for cooling the interiors of urban structures located in warm climatic regions. The need for cooling adds to the building maintenance cost, increases the building’s carbon footprint, and contributes to air pollution.

The above phenomena and issues have been well recognized for over four decades.3 To mitigate the problems associated with excessive solar heating, solar reflective and heat emission technologies have been developed and widely adapted for roofs and, to a significant extent, to pavements.3-9 According to the Cool Roof Rating Council’s (CRRC) website,10 currently there are 3180 certified roof coating products. Due to the heightened awareness of global warming and ever-rising energy costs, there is a need to extend solar reflective technologies beyond roofs and pavements to other surfaces, such as exterior walls. According to a recent study by Lawrence Berkley National Laboratory’s Heat Island Group, there is great untapped potential for cool coatings for walls.11 However, there are only a few solar reflective coating products for walls, and only 147 certified products are listed on the CRRC website. A literature survey has shown that, although there is increased research activity on heat-reflective coatings for walls, formulation data for commercially viable exterior wall coatings are very limited. The primary objective of this study is to contribute to filling this knowledge gap and enable formulators to develop their own successful products.

Initially, the study focused on understanding and quantifying the heat-reflective performance of conventional waterborne exterior architectural coatings and optimizing the formulations for solar reflectance without the use of specialty heat-reflective materials. All experimental coatings were prepared according to commercially viable formulations. In addition to solar reflectance, other key properties of the coatings, both at wet state and as dry films, were monitored. Results from these types of studies should enable formulators to select solar reflective grades of common raw materials while retaining other important coating properties. The solar reflective materials studied include hollow-spherical inorganic and organic particulate fillers and mixed-metal oxides.

The rheology modifiers used in all formulations in this study are associative thickeners that are sensitive to many formulation variables, including the colorants. As our previous studies have demonstrated,12 this sensitivity used to be a huge problem causing unpredictable viscosity drops of tint bases when tinted with predispersed colorants. A secondary objective of the current study is to assess the magnitude of the associative thickener sensitivity to today’s colorants, both conventional and solar reflective.

Experimental Materials and Methods

All raw materials used in formulating the coatings are routinely used by the paint and coating industry and were obtained from commercial suppliers. The initial filler (calcium carbonate and nepheline syenite) evaluations were conducted with an exterior flat white formulation, at a pigment volume concentration (PVC) of 43.4 containing predispersed TiO2 and filler (Base Formulation 1 (BF1)). The next set of formulations was prepared with TiO2 in dry powder form (BF2). An example of the latter type, 25 PVC formulation, is shown in Table 1. Our most recent experiments were conducted with a 17.5 PVC, direct-to-metal (DTM) formulation identical to a published study.13 Formulations were mixed with an EMI MXML-STD disperser using a Cowles type blade in pint-sized paint cans at approximately 400 g total weight. The grind step was conducted at 1600 rpm and the let-down step at 1000 rpm.

 

Continue reading in theissue of CoatingsTech

]]>
Methods to Determine Open Time of Architectural Coatings /coatingstech-magazine/articles/methods-to-determine-open-time-of-architectural-coatings/ Wed, 27 Aug 2025 18:06:43 +0000 /?post_type=ct_articles&p=252478 By Jennifer Mills, John Rabasco, Sunny Wang, Wesley Rauenzahn, and Scott Purtell The Dow Chemical Company

Introduction

In this article, we introduce a new applied method, brush workability, for determining the open time of architectural coatings, that offers good reproducibility and high level of differentiation in lab testing. This method shows validated correlation to real world application, using a selection of commercial paints in a double-blind contractor study.

Open time in architectural coatings is defined as the time after applying a single coat of paint where the film remains wet and workable. It is distinct from the full cure time or time before a second coat may be applied. Poor open time is evidenced by the inability to smoothly blend two areas of coating on a large substrate (within a single coat) and is also correlated to poor leveling as the film dries which can result in brush marks or visible roller pattern. Open time can also be evident during the coating application, where paints with poor open time may exhibit roller picking and poor drag between the drying film and the brush or roller.

There are multiple stages in paint drying, including: (1) Diffusion of water through the coating to the air interface and evaporation; (2) Film compaction and particle jamming; (3) Latex particle deformation under capillary force; final evaporation of water; and (4) Final cure/film compaction and coalescence via polymer entanglement. 1-3 Workable open time is defined by the first two stages.

Current industry standards for measuring open time include ASTM methods such as wet edge,4 dry to touch (DTT),5 and use of automated dry time recorders.1 These methods may be subjective in the ways they are rated and/or applied. Furthermore, many scientists and customers have noted that such methods do not translate well to actual paint application and/or are not physically representative of practical workable open time. This underscores the need for better methods with reduced subjectivity and better correlation to real world application, such as our new method.

Materials and Methods

Table 1 details the commercial paints used in this study, with information on technical properties. All paints are eggshell sheen, interior paints. Paint viscosities were measured using the lab viscometers (KU Stormer, ICI, Brookfield LV3/6 rpm). All testing was performed blind, using the paint IDs in Table 1 such that the applicator did not know which commercial paint was being tested. All lab open time tests were performed in a temperature-controlled lab at 75 °F and 50% RH.

Wet Edge: The wet edge test is adapted from ASTM D7488, using two vertical parallel lines running the length of the chart rather than six independent X marks at each time point. Paint was drawn down on a Leneta BK chart using a square bar with 5-mil gap. Immediately following the drawdown, the timer was started and two lines were drawn down the center of the wet film using two parallel tongue depressors. At 1-min intervals, the wet film was brushed over with 15 brush strokes in one direction. The brush was not dipped in fresh paint each time, ensuring a harsher, quicker test. The wet edge open time is the last time when the vertical lines are not able to be seen.

Dry to Touch (DTT): DTT testing was performed using 3 mil drawdowns on BK charts. Following the drawdown, a gloved fingertip was placed in the center of the wet drawdown at 1-min time intervals, and then the wet fingertip was pressed on the chart outside the drawdown area to leave a fingerprint. The paint is considered dry to touch when no finger mark is left. This method is adapted from ASTM D1640.5

Automated Dry Time Measurements: A Gardco circular path dry time recorder was also used for automated drying time measurements of paints. The machine consists of a Teflon ball stylus with a weight on the arm to control force, which moves in a circle through the wet film at a set speed. Tests were done using the 1-h setting, and 5-mil drawdowns on BK charts. The stylus was set approximately in the middle/center of the drawdown. Once complete and dry, the dry path was inspected for four types of signatures according to ASTM procedure D5895.1 There is a transparent overlay to mark the time points corresponding to the positions of each signature.

Continue reading in the issue of CoatingsTech

 

]]>
Reinvestigating the Link Between Lab Test Results and Real-World Exposure: A Study on Grain Cracking Performance of Architectural Paints /coatingstech-magazine/articles/reinvestigating-the-link-between-lab-test-results-and-real-world-exposure-a-study-on-grain-cracking-performance-of-architectural-paints/ Fri, 02 May 2025 14:43:48 +0000 /?post_type=ct_articles&p=251389 Xin Li,Keith Task,Shawn Overcash,Jack Johnson, andNicholas FoleyBASF Corp. USA

Correlating paint film integrity in the lab with wood grain crack resistance in real-world exposure is a challenging task. In 2020, we reported on early correlations between adhesion and film mechanics that when combined could fit a grain cracking predictive model to outdoor weathering.¹In this study, we sought to further challenge our own model by greatly expanding our study to include 79 more paints on various substrates. Our aim was to elucidate potential correlations between paint film mechanical properties and realworld exposure performance and to test the validity of our early model.

Through our analysis, we identified several significant factors and developed a statistical model. Although it is still in its early stages, this model shows promise in providing insights into the performance of paints under real-world exterior conditions. Further refinement and validation of this model could have significant implications for the paint industry. Such a model could enhance the durability and quality of wood coatings and accelerate the development timeline.

Introduction

The correlation between laboratory tests and real-world applications of paint is a critical area of research within the paint industry. While laboratory tests provide valuable insights into paint properties and performance in controlled environments, they often fail to accurately replicate the complex and dynamic conditions found in real-world environments.² Consequently, investigating the correlation between laboratory results and real-world scenarios, particularly concerning grain cracking in paint, becomes essential.

Grain cracking is a prevalent issue that occurs when paint applied to dimensionally unstable wood substrates undergoes cyclic stress from temperature fluctuations, moisture, and other environmental factors. However, reproducing these conditions accurately within a laboratory setting proves challenging, potentially leading to results that do not truly reflect the behavior of paint in the field. Understanding the correlation between laboratory tests and real-world applications of paint becomes critical in developing more accurate and reliable testing methods, as well as improving paint design and formulation. By studying this correlation, researchers and professionals in the paint industry can develop more effective strategies for preventing grain cracking and other forms of paint degradation. This, in turn, leads to enhanced durability, aesthetics, and overall quality of paint products. Therefore, investigating the relationship between laboratory tests and real-world applications is a vital endeavor that holds significant implications for the paint industry and its consumers.

In our previous study, we focused on evaluating the mechanical performance of 18 different paints.¹ The aim was to establish correlations between the performance of these paints and their real-world exposure results. To achieve this, we employed multiple linear regression (MLR) models. During the course of our research, we discovered that the results obtained from various laboratory and accelerated test methods were significantly confounded. These results did not yield easily decipherable trends.

To overcome these challenges, we expanded our study to include additional parameters. Specifically, we measured the tensile elongation at multiple conditions, adhesion to water-conditioned surfaces, and film hardness. By incorporating these factors, we were able to develop a predictive model that exhibited a high degree of accuracy. It is important to note, however, that this model is currently limited to the scope of a single commercial paint study.

To progress the development of highperformance exterior wood coatings, it is crucial to validate and expand on our findings. This entails conducting a similar study that encompasses a broader range of paints, covering a wider spectrum of mechanical performance. By doing so, we can further investigate and identify correlations between mechanical properties and real-world exposure results. This expanded research will ultimately serve to enhance the predictive model and transform it into a valuable tool for the development of high-performance exterior wood coatings.

In this study, we examined 79 paints with different formulations, colors, sheens, and significant variations in mechanical performance. These paints were applied to various substrates and evaluated every six months to determine if we could establish a correlation between accelerated testing and long-term real-world exposure results. This comprehensive analysis aims to provide a more robust understanding of the correlation between laboratory tests and real-world applications of paint, ultimately contributing to the advancement of paint technology and the development of superior paint products.

Experimental Setup
Paints
In this study, the 79 paints used included 16 experimental waterborne acrylic architecture paints and 63 commercial waterborne architecture paints purchased from hardware or paint stores. The paints were selected to cover a wide range of formulations, pigment volume concentrations (PVC), mechanical properties, and historical exposure results based on our own in-field benchmarking results. Table 1 provides information on the number of paints used in the study based on different sheens and bases. The sheens include semi-gloss, satin, and flat, while the bases include a white and deep (tinted with 12 oz per gallon black colorant) from each sheen.

]]>
A Study of the Effects of Siloxane and Silica Additives on Dirt Pick-Up Resistance in Low-VOC Exterior Architectural Coatings /coatingstech-magazine/articles/a-study-of-the-effects-of-siloxane-and-silica-additives-on-dirt-pick-up-resistance-in-low-voc-exterior-architectural-coatings/ Tue, 04 Mar 2025 18:28:55 +0000 /?post_type=ct_articles&p=250670 Sarah Hancock,Meixi Chen, andJ. Renae Bennett, Evonik Corporation, USA

As the coatings industry moves towards lower volatile organic content (VOC) or near-zero VOC, achieving good film formation in waterborne systems without sacrificing other coating properties has become challenging. Low-VOC coatings are softer and tackier due to the use of low Tg resin, which makes them more susceptible to capturing dirt and dust, especially in warmer and more humid climates. Of all the tradeoffs in low-VOC formulations, dirt pick-up resistance is one of the most noticeable changes, particularly in traditional exterior house paints. Although dirt pick-up is a complex process, the interaction of the resulting paint film with environmental particles, weather, and other variables is ultimately defined by the surface properties, which affect the accumulation of dirt. This study will explore the effects of siloxane and silica additive technologies on dirt pick-up resistance using an accelerated test method, and the mechanism of action of these additives will be discussed.

Introduction

Dirt pick-up resistance (DPUR) is a topic of high interest in exterior architectural coatings. Consumers want paint that can resist staining while also being easy to clean. In developing dirt-resistant paints, outdoor exposure is necessary for providing real-world data; however, these tests can take many months, or years, before a coating’s performance can truly be understood. Hence, accelerated DPUR tests are critical to enabling formulation development and providing insights into how various components may contribute to the DPUR of a coating. Unfortunately, there is currently no standard accelerated DPUR method in the coatings industry; several methods focus on a dry deposition of a dirt source, meanwhile methods developed in wetter climates feature dirt application using a dirt/water slurry.1 In general, existing accelerated DPUR methods follow a procedure consisting of 1) applying the paints to panels, 2) curing the coated panels under conditions of controlled temperature and humidity, 3) exposing the cured panels to ultraviolet (UV) irradiation and higher temperature, 4) applying and removing the dirt from the conditioned panels, and 5) analyzing the extent of dirt pick-up and removal from each panel. However, the dirt application and removal step has been acknowledged to be the greatest source of low reproducibility for these methods.2 In this work, a new accelerated DPUR test method was developed to facilitate studying both initial pickup of dry dirt and how well that dirt could be rinsed off when subjected to a rinsing process.

While siloxanes have traditionally been utilized to enhance surface slip, flow, and leveling,3 recent research has demonstrated that siloxane surface control agents can also significantly boost block resistance of coatings.4,5 In a similar vein, spherical silica particles have been found to increase burnish and wet scrub resistance of architectural coatings due to their effect on the dry coating film.6 These results motivated us to investigate the impact of various polyether-modified siloxanes, emulsions of higher molecular weight and crosslinked siloxanes, aqueous dispersions of fumed silicas, and spherical precipitated silicas on dirt adhesion and its release.

Experimental

A commercial low-VOC waterborne, self-crosslinking acrylic exterior satin paint was chosen to evaluate various siloxane and dispersed silica additives. Siloxane-based surface control additives (SCAs) were post-added at 0.50 wt % to the commercial paint, mixed well, and the paints were allowed to stand overnight before use. Similarly, dispersed silica additives (DSAs) were post-added at 1.0 wt % to the commercial paint, mixed well, and the paints were allowed to stand overnight before use. The characteristics of the additives tested are summarized in Tables 1 and 2.

A low-VOC waterborne, self-crosslinking acrylic exterior flat paint with a 76% PVC was formulated (Table 3) and it was used to evaluate the effects of full volume-to-volume replacement of calcium carbonate filler with spherical silica fillers (SPHs) of varying particle size (Table 4). Similarly, once mixed, the formulations in Table 3 were allowed to rest overnight to release residual foam from mixing.

The commercial paint samples to which had been post-added various siloxane and dispersed silica additives and the coating formulations in Table 3 were applied to scrub charts using a 150-mm wide bird-type film applicator for a 4-mil wet film thickness. After two days of drying in a standard conditioning atmosphere of 21–25 °C and 45–55% relative humidity (ASTM D4332-22), the scrub charts were trimmed to the test panel size (12.7 cm x 10.8 cm; center of coating) and cured in a Q-SUN Xe-3 Xenon Test Chamber (Ser. No. 20-34603-79-X3HBSE; from Q-Lab) at 40 °C and 45% relative humidity using a full-spectrum sunlight filter with an irradiance of 0.89 W/m2 at 340 nm for three days. The test panels were removed and allowed to rest for two hours before dirt deposition. A number of studies have revealed that typical outdoor dirt particles that soil exterior coatings have a number median diameter of approximately 100 nm.7-9 Hence, for this study, Lamp Black 101 (carbon black from Orion Engineered Carbons), and BAYFERROX® 509 (iron oxide from Lanxess) were chosen. These dirts were applied via fine-mesh sifters to achieve a complete and uniform coverage of the test panels. After one day, the dirt was removed by lifting the panels upright and tapping 15 times against the benchtop. The panels were then rinsed at an upright position with 15 misting sprays of DI water from a spray bottle at a distance of 20 cm. The residual water was removed by tapping the panels 15 times, after which they were returned to a horizontal position and dried overnight.

]]>
Balancing Rain Resistance and Open Time with Diffusing Wave Spectroscopy and Conventional Application Tests /coatingstech-magazine/articles/balancing-rain-resistance-and-open-time-with-diffusing-wave-spectroscopy-and-conventional-application-tests/ Tue, 07 Jan 2025 17:16:59 +0000 /?post_type=ct_articles&p=249967 By Kaliappa Ragunathan, Nicholas Foley, and Sofia Goodrich-Accolla† BASF Corporation

Sufficient open time is essential for achieving painting efficiency and delivering aesthetically pleasing results in architectural coatings. The open time can vary widely for an exterior coating because the wet coat may experience extreme weather conditions from humidity and temperature changes to varying wind speeds. Additionally, the open timeof the coating can be influenced by solids, pigment volume concentration, polymer composition, rheology modifiers, additives like humectants, and solvents.

The open time and early rain resistance are seemingly diametrically opposed properties, and it is difficult to improve the early rain resistance without negatively influencing open time. Through the use of statistical design of experiments, this study identified polymer structure factors that can influence the open time and early rain resistance of the paints. The rain resistance was tested using the shower head test method, while the open time was tested using conventional methods such as ASTM 7488 and Gardco Quadracycle drying time.

Further insight on open time was gained by a novel test method using diffusing wave spectroscopy which provides information on critical steps of the film formation process such as water evaporation-concentration, particle packing, particle deformation, and film dry through. Combining this data with polymer structure study allowed for the elucidation of structure-property relationships, specifically regarding open time. The resulting novel insights helped in the development of new polymer prototypes that positively influence both early rain resistance and open time.

Introduction

Weather, especially rain, has a severe impact on the film formation of freshly applied paint on an exterior wall. A fastdrying paint will provide early resistance to rain. However, developing1,2a fast-drying paint with sufficient open time is challenging. The open time3of paints has been defined as the period of time during which a painter can make corrections to the freshly applied wet paint film without leaving brush marks. Sufficient open time is essential for achieving painting efficiency and delivering aesthetically pleasing results in architectural coatings. The open time of the coating can be influenced4,5by solids, pigment volume concentration, polymer composition, rheology modifiers, additives like humectants, and solvents.

Film formation6,7 from polymer dispersions is schematically depicted in Figure 1. It is expected that water-based paints undergo similar stages, such as water evaporation-concentration, particle packing, particle deformation, and particle coalescence-interdiffusion, to form a coating. The water evaporation stage strongly influences the open time of the paint. The drying conditions of the paint, including temperature, humidity, and air flow, have a significant impact on the water evaporation rate and open time. Low temperature, high humidity, and stagnant air will slow down water evaporation and increase open time. Conversely, high temperature, low humidity, and high-velocity air flow will speed up water evaporation and reduce open time.

FIGURE 1 Film formation in polymer dispersions.6, 7

In this research, we studied the polymer composition to improve the open time without compromising early rain resistance. Statistical design of experiments was used to identify polymer structure factors that can influence the open time and early rain resistance of the paints. Multi-speckle diffusing wave spectroscopy8,9 was used to gain understanding on the critical steps of the film formation process such as water evaporation-concentration, particle packing, particle deformation, and film dry through. Diffusing wave spectroscopy is an extension8 of classical dynamic light scattering to concentrated and opaque media. The diffusing wave spectroscopy and polymer structure factor data were analyzed to develop new polymers with improved open time without compromising early rain resistance.

Experiments

To study the effect of polymer composition on the open time and early rain resistance, a custom design of experiment using JMP® was carried out. The design consisted of eight structure factors of a control polymer dispersion and the details of the design are given in Table 1. Paint formulated using this control polymer provided better early rain resistance and equal open time compared to a leading national brand commercial paint. The goal is to improve the open time of this paint by changing the control polymer structure without reducing the early rain resistance of the paint.

Sixteen different polymer dispersions were synthesized using this design strategy and the composition differences of these polymer dispersions are given in Table 2. These polymer dispersions were synthesized by conventional emulsion polymerization using unsaturated monomers, emulsifiers, and initiators. These polymer dispersions have approximately 53% solids content. Two polymer dispersions, Nos. 1 and 14, were not stable and so they were eliminated from the study. For studying the main effects using this JMP® custom design, the minimum number of runs required is only 9.

]]>
Quantitative Image Analysis of Roller Application Performance /coatingstech-magazine/articles/quantitative-image-analysis-of-roller-application-performance/ Tue, 07 Jan 2025 16:54:41 +0000 /?post_type=ct_articles&p=249987 By Wenqin (Sunny) Wang, Amy Qin, Gerry Valdez, Sophie Kim, Sam Lim, Yicheng Hu, and Jennifer Mills, The Dow Chemical Company, USA

Introduction

Coatings’ application performance, such as ease of application, superior coverage, and faster return-toservice, continue to be a key consideration for both consumers and contractors when choosing architectural coating products. Based on the claim analysis of commercial architectural coatings, paint application related properties are among the top claimed product performance in architectural coatings, as shown in Figure 11 The rheological properties of coatings play critical roles in determining various aspects of coatings application, including sag and leveling balance, spatter resistance, application feel, roller pattern, and applied hide. In addition to rheology of coatings, paint application process and results are highly dependent on environmental conditions, roller cover, paint applicator, and substrates. Traditionally, evaluating the appearance of coating and spatter resistance has heavily relied on visual assessment, which could be influenced by inconsistencies in human visual perception. To address this, we have conducted a series of roller application studies in different formulation spaces and employed advanced image analysis technologies to enable more reliable and quantitative evaluation of spatter resistance and roller patterns. In this article, we will share the insights gained from our study and discuss the impact of rheology modifiers on the performance of roller applications.

FIGURE 1 Top paint claims from commercial architectural coating products in the market in 2023.

Introduction of Spatter Resistance

Spatter resistance is an important roller application property. Paint spatters are tiny droplets of liquid paint that can be ejected from the roller/substrate as coatings are applied on substrates. The liquid droplets can land on adjacent surfaces or areas not meant to be painted. Coatings with good spatter resistance will reduce the work associated with preparing the surface and cleaning up after painting as well as help painters get the work done more efficiently.

Spatter resistance is highly influenced by the rheology of the coatings. A series of rheology modifiers were evaluated in four different formulations, including standard acrylic interior flat formulations with or without hydroxyethyl cellulose (HEC), premium acrylic flat formulation, premium composite-forming acrylic flat formulation, and economy acrylic/PVA blend flat formulations with or without HEC. In addition, nine commercial paints from leading paint manufacturers were also included in the study as benchmarks.

Rheology modifiers that were evaluated included both hydrophobically modified ethoxylated urethanes (HEURs) and hydrophobically modified alkali-swellable emulsions (HASEs), with rheology profiles spanning from shear-thinning to more Newtonian. Roller application was conducted on primed drywall (4′ × 4′) using woven roller cover, 7″ long, 3/8″ nap. A professional painting contractor conducted all roller applications. For each roller application trial, two vinyl charts are taped at the bottom of the drywall panel to capture spatter of the coating. Figure 2 shows an example of paint spatters on a black vinyl chart from a commercial interior flat paint, which has poor spatter resistance. The white dots on the charts are the spattered paint droplets. The top portion of the chart is closer to the drywall, which showed more paint spatters. The number of paint spatters decreased as the distance from the drywall increased.

FIGURE 2 Example of paint spatters captured on a black vinyl chart.

Image Analysis Algorithm Overview

Spatter resistance is rated by evaluating the paint spatter on vinyl charts. Several factors are included for evaluation, including the number of paint droplets, the size of droplets, and the intensity or contrast of droplets vs. background. Traditionally, this evaluation is done by visual assessment, where an operator would assign a score based on a set of standards or industry guidelines. However, this approach is prone to inconsistencies due to human visual perception.

A robust method has been developed for quantifying spatter resistance using image analysis for the detection and rating. To ensure consistent lighting and imaging condition among different spatter charts, images are captured using an imaging station under controlled light environment and imaging parameters. The captured images undergo image-processing techniques, such as image thresholding, to remove background noise. A blob-detection algorithm is then applied to identify individual spatter droplets. The algorithm identifies the blobs or a group of white pixels to capture the spatter. The algorithm was further refined based on fundamental physics of spatter-droplet generation to exclude the experimental artifacts from the group of detected spatters. Most of the spatters that result from the paint application will be circular shaped because the droplets experience free fall before landing on the test panel. The angle of incidence on these droplets can be assumed to be +/- 20 degrees, which will keep most of the droplets in a circular shape with constant diameter. On the other hand, experimental artifacts or unintentional paint marks on the test panel mostly occur in the form of streaks with large aspect ratio. Figure 3 shows the original image of the black vinyl chart that has undergone spatter-resistance testing on the left and the processed image with the detected spatters on the right. The figure shows one of the experimental artifacts in a non-circular shape located in the upper right corner. The blob detection highlights paint spatters in red circles, and the algorithm successfully identifies the experimental artifact, which was not included in the detection.

 

]]>
CRRC Surpasses 100 Wall Product Ratings /coatingstech-magazine/articles/crrc-surpasses-100-wall-product-ratings/ Thu, 19 Sep 2024 21:26:34 +0000 /?post_type=ct_articles&p=248668 Since its launch in September 2022, the (CRRC) has issued third-party product ratings for more than 100 exterior paint and siding products on the CRRC Rated Wall Products Directory (Wall Directory). As of July 30, 2024, there are 111 rated products spanning seven manufacturers and two product categories: architectural coatings and metal siding.

CRRC Wall Product Ratings are obtained through participation in the CRRC Wall Product Rating Program. The CRRC began accepting Wall Product Rating applications in January 2022 after years of development by experts. The program is overseen by the CRRC Wall Rating Program Committee.

The Wall Directory provides verified ratings of products’ solar reflectance and thermal emittance, informing design professionals and consumers about a product’s ability to reflect solar energy away from a building and cool itself by radiating absorbed heat. These properties improve resilience to heat, mitigate the urban heat island effect, and reduce cooling energy use. Exterior “cool” walls are promoted by standards, energy and building codes, and programs such as LEED.

To learn more, visit . Educational resources are available for policymakers and developers.

]]>
Initiative Aims to Empower Renters /coatingstech-magazine/articles/initiative-aims-to-empower-renters/ Thu, 08 Aug 2024 20:02:24 +0000 /?post_type=ct_articles&p=248128 image of bedroom with a white wall and dark wall

Images courtesy of Benjamin Moore

Benjamin Moore recently announced aimed at encouraging renters to personalize their living spaces using paint, while also addressing concerns about losing security deposits when moving out.

The company will offer up to 10,000 renters in the United States, Canada, and the United Kingdom a chance to redeem a free gallon of Regal Select Interior Ready-Mix White paint if they purchase a gallon of Benjamin Moore Regal Select Interior paint in August 2024. The complimentary gallon can be redeemed between July 15, 2025, and September 15, 2025, providing renters with the means to repaint their walls back to their original color before moving out.

Harriette Martins, senior vice president of Marketing at Benjamin Moore, noted that many renters hesitate to paint their homes due to concerns about restoring the rental to its original condition. “Using premium quality paints gives renters the confidence to transform their spaces without worrying about the end of their lease,” she said.

Regal Select Interior is marketed for its durability, scuff resistance, and ease of maintenance, which the company says is due to its proprietary stain release technology that delivers excellent durability and washability. The paint is available in various sheens and more than 3,500 colors, which the company says makes it suitable for high-traffic areas such as living rooms and kitchens.

Michelle Griffith, an agent with Douglas Elliman Real Estate, praised the initiative, suggesting it could help renters feel more at home without risking their security deposits.

More details on the initiative and redemption process can be found at benjaminmooregiveaway.com. Information about local retailers is available at .

]]>
Expanded Use of Powder Coatings in the U.S. Architectural Market /coatingstech-magazine/articles/expanded-use-of-powder-coatings-in-the-u-s-architectural-market/ Tue, 09 Jul 2024 20:22:17 +0000 /?post_type=ct_articles&p=247733 Eric Casebolt, ChemQuest Powder Coating Research

Coatings Xperience: Informed commentary on the coatings industry

Over the past couple of years, there has been increased interest in R&D activity for powder coatings used in architectural applications in the U.S. market. From the perspective of industrial coatings, the architectural segment comprises coatings applied in a factory environment for use in building and construction applications.

For the purposes of this column, we will focus our discussion specifically on coatings applied to aluminum extrusions that are used in the manufacture of building products, which is the highest volume and value application in the architectural coatings segment. These coated aluminum extrusions are used as the structural component for a variety of architectural products, including doors and windows, store fronts, and curtain walls that define the façade of most high-end commercial buildings constructed today.

The coatings that are used on these products are either solvent- based or powder coatings that are applied in a factory environment, which includes a pretreatment process of up to seven stages, followed by a highly automated coating process. The pretreatment and coating process is specifically designed to ensure the highest level of quality because the coated architectural components will be used on high-value assets, such as stadiums and skyscrapers, which will be exposed to harsh environments for an extended period.

In fact, to be considered an approved applicator for the architectural segment, the coating application process is audited by the coating supplier. The audit process helps to ensure quality is consistent and performance meets specifications as outlined by the Fenestration & Glazing Industry Alliance, commonly known as AAMA standards.

Key Growth Drivers

Now that we have defined the market segment, let’s dig into the reasons behind the increased activity in this segment. At ChemQuest, we see two main drivers:

  • High growth potential of powder coatings in architectural applications in coming years.
  • Uncertainty in the highend AAMA 2605 segment created by potential PFAS regulations.

The growth potential of powder coatings is predominantly due to their environmentally friendly profile compared to solvent-based coatings. Although coatings experts often debate the math behind which technology is more “sustainable” or “environmentally friendly,” decision-makers along the architectural value chain generally perceive powder coatings to be the technology of choice when sustainability is the top priority.

In the United States, however, powder coatings only account for an estimated 25% of the value of coatings over extruded aluminum for architectural applications. For comparison, powder coatings are the dominant technology in the Western European architectural segment, with widespread use over aluminum extrusions.

While various factors could account for powder coatings being used more broadly in Western Europe, ChemQuest has interviewed architects and architectural component suppliers who usually attribute the preference to Western Europe being further ahead in its sustainability efforts in building and construction—however ambiguous the term “sustainability” may be. It follows then, that as sustainability in building and construction becomes more of a priority in the United States, these value chain members will increasingly specify powder coatings to be used on their products.

The second driver behind the increased interest is pending PFAS regulations that could potentially impact the coatings that are used in the AAMA 2605 segment of the market, which is the highest performance standard and includes a 10-year weathering requirement. All powder coatings and solvent-based coatings that currently meet the AAMA 2605 specification use fluoropolymers as their base resin because of their ability to meet the longterm weathering requirement.

Under the broad-brush PFAS regulations that are currently proposed, these polymers would be banned from usage once regulations go into effect. To be clear, many scientifically sound arguments are being made that would exclude these fluoropolymers from any upcoming PFAS regulations—and this is certainly within the range of possible, if not probable, outcomes. However, with the long testing cycle and the high value of the coatings used in the AAMA 2605 segment, coatings companies and raw material suppliers are compelled to develop potential replacement materials to ensure they are either able to take advantage of the regulations or have a plan in place should regulations affect their products.

When trying to understand the potential changes in coatings technologies used in the architectural coatings market, business-savvy folks often ask the question: Who makes the decision on which coating technology is used on construction projects? This is an important question because if one wants to influence the use of their technology in the market, they need to determine who must be convinced that their technology has the strongest value proposition and warrants consideration.

For mass-produced products, which we will define as standard architectural components in stock colors, the architectural component supplier (façade or glazing manufacturer) makes the decision on which coating technology is used on their products, regardless of whether they are applying the coating in-house or if the coatings are applied externally. However, on custom-made or mass-produced products with custom colors, which are often referred to as “project-based” products, the decision process is not so clear. To keep the discussion at a high level, we will consider three potential decision-makers: building owners, architects, and architectural component suppliers.

Building Owners

Building owners have the highest level of decision-making power as they can make a unilateral decision on what coating is used on their building. However, this decision-making power is seldom used and only happens in practice if the building owner is on the extreme high end of the sustainability-minded population.

Even in that case, the building owner deciding on which specific coating or coating technology is used on their building is very rare. With that said, if one was able to convince building owners—or third-party organizations that can influence building owners—that a certain coating technology should be used based on sustainability merits or another value proposition, building owners could make that decision.

Architects and Architectural Component Suppliers

Architects have the secondhighest level of decision-making power and are often mentioned as the key decision-maker because they are responsible for specifying the coating. While it is true that they specify the coating, there are a couple of caveats that must be considered.

First, architects often specify a coating by the AAMA specification and do not include any details about the technology—powder or liquid—that must be used. Furthermore, even in cases when they do specify the coating technology, it is often followed by the term “or equivalent.” This gives architectural component suppliers the ability to use whatever coating technology they choose as long as it meets the AAMA specification and aesthetics as required by the architect. Because of these two caveats, it is most often the architectural component supplier that makes the final decision, even though there are two parties in front of them that could dictate which coating technology is used.

Innovating for the Future

While uncertainty remains regarding whether fluoropolymers used in AAMA 2605 architectural applications will be included in upcoming regulations, it is clear that this is a market where powder coatings will continue to grow at a faster rate than solvent-based coatings. When change and uncertainty exist in these types of high-end markets, the result is often increased R&D activity as companies try to capitalize on the change or prepare to launch new products should their current products be impacted.

The architectural construction market involves a complex decision-making process. ChemQuest remains optimistic about the segment’s future and is actively engaged to provide assistance with new product development or help teams navigate the market activation process.